We seek to understand and document all radio transmissions, legal and otherwise, as part of the radio listening hobby. We do not encourage any radio operations contrary to regulations. Always consult with the appropriate authorities if you have questions concerning what is permissible in your locale.

Show Posts

This section allows you to view all posts made by this member. Note that you can only see posts made in areas you currently have access to.


Messages - JethTran

Pages: [1]
1
Hi.... I've never seen a 240V Three-Phase framework introduced ungrounded. I've worked with 480V ungrounded frameworks a considerable amount and just know about one catastrofic disappointment.

Administration coherence is the solitary advantage of an ungrounded framework. The weaknesses are: transient overvoltages are not controlled, framework voltages over the ground are not controlled. The ungrounded framework is entirely coupled to ground. Were administration progression is required an ungrounded framework is protected as I would like to think, if the appropriate strategies are utilized, for example ground locator lights, find and right ground-blames when useful, and so on

Does your client have a real requirement for an ungrounded framework? Assuming not, I would suggest a grounded framework. Corner establishing presents different issues, for example no breakers whenever grounded stage is interuppted (should open all stages). You could utilize a crisscross transformer to ground the framework however it is smarter to simply supplant the 75 kVA xformer with a 240V 3-Phase 4-Wire xformer.